      Good afternoon,

      Are there any specific requirements for using the inputs on the same pin as the PLC for FlexCase G? 12 and 13? Does the PLC have to be enabled to for those to function?

    • AmirFAmirF
      Moderator
      Post count: 31

      Hi Mathew,

      The control pilot pin on FCG is muxed with DI12(pin B45).
      Also, ADC12(pin A26) acts as a Proximity Pilot with a 1/2 voltage divider ratio.
      You don’t need any activation for either pins, which are activated by default.

      Cheers,
      Amir